Hey All,
Debate at the shop is we have a 3 story Multi Family Building and we have some NM run in the shared corridor. The NM is about 12' up, but the ceiling is a grid drop to 9'.
We all agree that in "other than dwellings", this is not allowed. However, the exception for NM allows for it to be above the grid in a residential setting/ dwelling. From the commentary of the 2020 NEC, we see that the entirety of the building is included as being part of said residential setting/ dwelling. The Multi- Family definition also indicates it is a BUILDING containing more than 3 dwelling units, thus including the common areas.
The dilemma is the AHJ is trying to decide whether or not the NM needs to be protected or moved. He is saying the common areas are NOT part of the dwelling(s). While I concede the corridor is NOT part of the dwelling UNIT, it is still part of the building. Which is defined as being part of the overall dwelling.
Article 334 seemingly leaves this all open to interpretation and semantics.
I hope I have given enough information to start the debate. Basically, can we have the NM in the common areas above the drop lid or does said NM need to protected to be in compliance?
Cheers...
Debate at the shop is we have a 3 story Multi Family Building and we have some NM run in the shared corridor. The NM is about 12' up, but the ceiling is a grid drop to 9'.
We all agree that in "other than dwellings", this is not allowed. However, the exception for NM allows for it to be above the grid in a residential setting/ dwelling. From the commentary of the 2020 NEC, we see that the entirety of the building is included as being part of said residential setting/ dwelling. The Multi- Family definition also indicates it is a BUILDING containing more than 3 dwelling units, thus including the common areas.
The dilemma is the AHJ is trying to decide whether or not the NM needs to be protected or moved. He is saying the common areas are NOT part of the dwelling(s). While I concede the corridor is NOT part of the dwelling UNIT, it is still part of the building. Which is defined as being part of the overall dwelling.
Article 334 seemingly leaves this all open to interpretation and semantics.
I hope I have given enough information to start the debate. Basically, can we have the NM in the common areas above the drop lid or does said NM need to protected to be in compliance?