W wyatt Senior Member Nov 2, 2005 #1 In 334.15(B)[2005] what is ment by Schedule 80 pvc for protection can I not use Sceduel 40 on a wall exposed?
In 334.15(B)[2005] what is ment by Schedule 80 pvc for protection can I not use Sceduel 40 on a wall exposed?
W websparky Senior Member Location Cleveland, Ohio Nov 3, 2005 #2 Re: NM cable and PVC Schedule 80 is approved for protection because it is stronger than 40. Also,don't forget "or other approved means".
Re: NM cable and PVC Schedule 80 is approved for protection because it is stronger than 40. Also,don't forget "or other approved means".
H hurk27 Senior Member Location Portage, Indiana NEC: 2008 Nov 4, 2005 #3 Re: NM cable and PVC Only if the raceway is located in a place where it is subject to physical damage would schedule 80 be required, Of course its a AHJ call for that. [ November 04, 2005, 07:04 PM: Message edited by: hurk27 ]