stickboy1375
Senior Member
- Location
- Litchfield, CT
iwire said:So now that you know it's wrong how about figuring a code compliant way to do it?
Why would he do that? He does not care.
iwire said:So now that you know it's wrong how about figuring a code compliant way to do it?
HaskinsElectric said:The only reason they aren't by the way, is because they want to sell more 2-Screw connectors.
I use a 2" chase nipple with a locknut and a plastic bushing and just stuff my cables through it and into the panel. The cables are supported within 8" of this opening.
Is this a code compliant installation?
HaskinsElectric said:In the past I would jam as many NM cables into a 2-Screw Romex connector(s) as I could. But an Inspector pointed out that they weren't listed for so many cables. The only reason they aren't by the way, is because they want to sell more 2-Screw connectors. But anyway, now I use a 2" chase nipple with a locknut and a plastic bushing and just stuff my cables through it and into the panel. The cables are supported within 8" of this opening.
Is this a code compliant installation?
stickboy1375 said:check out 312.5 (C)
HaskinsElectric said:"Openings through which conductors enter shall be adequately closed"
That's an interesting code section. Seems highly subjective. Maybe a wad of spackle or Duct Seal would do?
HaskinsElectric said:"Openings through which conductors enter shall be adequately closed"
That's an interesting code section. Seems highly subjective. Maybe a wad of spackle or Duct Seal would do?
Edit: Whoops, I just quoted 312.5(a) not (c). However, it seems the exceptions to 312.5(c) allow this practice. Whoops, wrong again, the nipple must be at least 18" in length. Yup, my installation is not code compliant.
HaskinsElectric said:Edit: Whoops, I just quoted 312.5(a) not (c). However, it seems the exceptions to 312.5(c) allow this practice. Whoops, wrong again, the nipple must be at least 18" in length. Yup, my installation is not code compliant.
iwire said:Sound like you need more inspections.![]()
iwire said:So now that you know it's wrong how about figuring a code compliant way to do it?
peter d said:Probably because it's an acceptable practice in Arizona and until that changes 220/221 and thousands of other EC's in the state are going to keep doing it that way.![]()
stickboy1375 said:The only problem I have is why they find it acceptable?
I understand why they do it, but did the state get up one day and say "Hey you know what, lets make life easier on the electrician and let him just use giant snap in bushings..." :grin:peter d said:I think it has to do with the fact that their panels are surface mounted outside, and that is the easiest and fastest way to enter the cables into them.
peter d said:and that is the easiest and fastest way to enter the cables into them.
iwire said:Oh, I see, we only follow the easy codes. :grin:
stickboy1375 said:I'm just wondering if the inspectors know its a violation or not... If everyone does it, it must be legal mentality.
peter d said:I think once something becomes such an acceptable way to do something, it would be pretty hard to stop it.
So now that you know it's wrong how about figuring a code compliant way to do it?
each cable shall be secured to the cabinet or cutout box