@MChav841 NM is the least of your problems if your feeding 157 volts into one input.
You're right, suemarkp, it is #12.Isnt yellow usually #12? Not that it matters though. And it doesnt appear to be secured every 4 feet either.
If your not going to do rapid shutdown I'd still split it into two strings.You're right, suemarkp, it is #12.
Tortuga, the Anker Solix F3800 Plus takes from 11v - 165v. The older F3800 is the unit that can only take up to 60v.
Needless to say, I'm disappointed again. They were supposed to come Saturday (yesterday) to put in the correct wire, but didn't show up.
What has the number of strings got to do with whether or not RSD is required?If your not going to do rapid shutdown I'd still split it into two strings.
Not really, the real issue is that NM cable is not allowed to be used for PV DC circuits inside buildings, as they have to be in metal raceway. My view is NM cable is permitted to be used for microinverter AC circuits that extend from interior spaces into rooftop surface mount J-boxes beneath arrays, like from EZ Solar or Soladeck, or similar. NM cable entering such a surface mount box under an array is not considered an outdoor wet space as far as I am concerned, no different than NM cable entering surface mount boxes for receptacles or lighting on the outside of a home, which exists in every single home that is out there. If it were not a surface mount Jbox, and there were conductors running to the Jbox outdoors in a raceway, that would be considered outdoor wet, in my opinion.From a code standpoint, your concern is 100% valid. 14-2 NM (Romex) is not allowed in outdoor, wet, or rooftop-exposed locations. It’s only permitted in dry indoor spaces, like inside walls or in a dry attic. So the real issue isn’t that it’s a solar system — it’s where the cable is being used.
On the roof and through the roof penetration: you should see PV wire, USE-2 cable, or THHN/THWN-2 in conduit. Once the wiring has entered a dry attic space, transitioning to NM cable can be acceptable. Also, your array is roughly 157V and 13.25A wired in series.
Even though 14 AWG is typically rated for 15A, solar circuits are treated as continuous loads, so code requires a 125% factor. That puts your effective current around 16.6A, which is really pushing (or exceeding) what 14 AWG should be carrying.
Using NM in a dry attic for a short run can be OK, but using NM on the roof or outdoors is not code-compliant. For an array like yours, 12 AWG THHN/THWN-2 or PV wire would be the safer and more correct choice
Would a system whose voltage never exceeds 80 volts not inherently comply with 690.12(B)(2)?What has the number of strings got to do with whether or not RSD is required?
It would. I have seen several inverters over the decades designed for low voltage high current arrays. They never catch on since the fat conductors required eat up all the savings in other areas. The electronics required for the high current switching also limit the inverter power.Would a system whose voltage never exceeds 80 volts not inherently comply with 690.12(B)(2)?
It would satisfy (B)(2) but not (B)(1), not more than 30V outside the array.Would a system whose voltage never exceeds 80 volts not inherently comply with 690.12(B)(2)?
Ok right not to derail the thread but as a thought experiment, say the OP split into two strings to get under 80 volts and set two fused disconnects at the array boundary.It would satisfy (B)(2) but not (B)(1), not more than 30V outside the array.
Ok right not to derail the thread but as a thought experiment, say the OP split into two strings to get under 80 volts and set two fused disconnects at the array boundary.
After the array disconnect is it just a DC feeder then?
A dwelling is not prohibited from having any number circuits or feeders with 120 VDC 'between conductors' [ 210.6(A) ] that remain energized when a the service (if any) is shut off.
No other system I think of in the NEC has such a restriction.