Re: NM cable in EMT
Wow, this post has gone a lot of places, here is the original post
Posted By MarkF
As to running NM or UF in EMT
NEC 2002 358.22 "Cables Shall be permitted to be installed where such use is permitted by there respective code articles"
340.10(4) When installed as Non metallic sheathed cable....shall comply with article 334
334.15(B)Protection from physical damage.
IMO to be code compliant all you have to do is say "I am protecting it from physical damage"
Certainly that was what the original post was doing and that would be what I do when I come down the surface of a wall down to a outlet.
I do not think anyone wants to run NM or UF in raceways or sleeves just for the fun of it.
334.15(B) does not say a maximum length that you can do this.
I hope they make this more clear in 2005 as it was clear in the 1999 book.
Wow, this post has gone a lot of places, here is the original post
Posted By MarkF
I would have to agree this would be a wet or damp location, I have not found raceways to stay dry when outside, no matter how carefully installed.Here's an old question that has been around for years. We are installing alot of air conditioner circuits for a local AC contractor. Most of the time we are able to get the circuit through the basement directly to the back of the disconnect. However, there are times that we have to run an additional 10-30 feet on the outside of the house. The local AHJ has demanded that we install a j-box on the outside and convert to THWN conductors. He has admitted that this is not in the code book (NEC) but he read an article on it and the writer "suggested" that NM not be run in conduit because it is not Wet of damp location rated.
Has anyone run into this before? I have been an electrician since 1973 and this is a first for me.
Thanks for your comments
Mark
As to running NM or UF in EMT
NEC 2002 358.22 "Cables Shall be permitted to be installed where such use is permitted by there respective code articles"
340.10(4) When installed as Non metallic sheathed cable....shall comply with article 334
334.15(B)Protection from physical damage.
IMO to be code compliant all you have to do is say "I am protecting it from physical damage"
Certainly that was what the original post was doing and that would be what I do when I come down the surface of a wall down to a outlet.
I do not think anyone wants to run NM or UF in raceways or sleeves just for the fun of it.
334.15(B) does not say a maximum length that you can do this.
I hope they make this more clear in 2005 as it was clear in the 1999 book.