Just curious, when did the insulation on the conductors of NM become 90 degree C and THHN?
I understand that. But the individual conductors are THHN. When did the individual conductors become THHN. I see older romex with thicker insulation on the individual conductors. Just curious.
So basically romex installed from 1986 on is rated at 90 degree C? It would be safe to install a dimmer with this type of wiring? The dimmer states the wiring must be rated fo 90 degree C.
Well said.
336-26. Conductors. The insulated conductors shall be one of the types listed in Table 310-13 which is suitable for branch-circuit wiring or one which is identified for use in these cables.
Conductors shall be rated at 90 degrees C. The ampacity of NM and NMC cable shall be that of 60 degrees C and shall comply with 310-15.
In the mid-1980?s, the outer jacked of this cable changed from an impregnated, braided covering to polyvinyl chloride (PVC), and the internal conductor insulation went from a 60[FONT=WP MathA,WP MathA]E[/FONT]C to a 90[FONT=WP MathA,WP MathA]E[/FONT]C rating. This newer cable is typically referred to as Type NM-B.
The oldest NEC code book that I have is 1987 and it states:
336-2 Construction. Conductors of Types NM and NMC shall be one of the types listed in Table 310-13 which is suitable for branch-circuit wiring or one which is identified for use in these cables. The ampacity of Types NM and NMC cable shall be that of 60?C (140?F) conductors in Table 310-16.
336-2 Construction. Conductors of Types NM and NMC shall be one of the types listed in Table 310-13 which is suitable for branch-circuit wiring or one which is identified for use in these cables. Conductors shall be rated at 90?FC (190?F). The ampacity of Types NM and NMC cable shall be that of 60?C (140?F) conductors in Table 310-16.
You could always add one.It is strange that my '84 does not have the vertical bar along the margin indicating the change.