paullmullen
Senior Member
- Location
- Wisconsin
- Occupation
- Electrical Engineer & Master Electrician
I was watching a video of a well-known electrician doing an installation of the Ford Charge Station Pro. The charger is rated at 80A and since charging can often take more than 3 hours, it is a continuous load. Thus, the branch circuit should be sized for 80A x 1.25 = 100A.
The demonstrated installation was completed using 3AWG NM Cable. Per 344.80, "the allowable ampacity shall not exceed that of a 60-degree C rated conductor."
The installer showed that the cable was rated at 90-degrees C (NM-B) and evidently the connectors are also rated at 90-degrees.
At 90-degrees, the ampacity of 3AWG cable is 115A, but it is only 85A at 60-degrees C.
At 60-degrees, the ampacity of 1AWG cable is 110A.
(From Ampacity tables in Article 310.)
I suppose that he may have been using some cable type other than NM, but that's what it looked like and the teacher was not specific.
I assume that he was doing it correctly and I'm missing a finer point. Can someone point it out?
Paul
The demonstrated installation was completed using 3AWG NM Cable. Per 344.80, "the allowable ampacity shall not exceed that of a 60-degree C rated conductor."
The installer showed that the cable was rated at 90-degrees C (NM-B) and evidently the connectors are also rated at 90-degrees.
At 90-degrees, the ampacity of 3AWG cable is 115A, but it is only 85A at 60-degrees C.
At 60-degrees, the ampacity of 1AWG cable is 110A.
(From Ampacity tables in Article 310.)
I suppose that he may have been using some cable type other than NM, but that's what it looked like and the teacher was not specific.
I assume that he was doing it correctly and I'm missing a finer point. Can someone point it out?
Paul