Can you elaborate on this? I don't touch Romex if I can help it.So I don't see those bags, but I would think those stackers "maintain spacing" and in between studs would be enough to satisfy the bundling requirement. Saying to "observe" 310.15 doesn't necessarily mean the stackers don't maintain spacing. If it does mean that, then at what point are wires or cables no longer "bundled"?
http://multimedia.3m.com/mws/mediaw..._UoYTSev7qe17zHvTSevTSeSSSSSS--&fn=SIFSDS.PDF
See page two, look for the fine print.
310.15(B)(3)(a)(4) used to be an exception that clarified that cables loosely traveling in the same direction for 24" required derating. Now it's less clear, for clarity, but the principle is still there. Imagine a gaggle of MC cables on bridle hooks - to say they are "touching" much less "bundled" defies common sense, but as far as the Code is concerned, they are. Now remove the MC and replace it with NM - no allowances.