NM Cable

Status
Not open for further replies.

newt

Senior Member
Can anyone tell me a section in the code that tells me how many nm cables allowed in bored holes.I limit the number to 3.Any ideas,thanks.
 
Re: NM Cable

It is not addressed. The only thing that is close is the required ampacity adjustment of the conductors if they are bundled longer than 24". See 310.15(B)(2)(a).
 
Re: NM Cable

There would be a practical limit based on the width of the member and the need to maintain the required spacing from the edge.
 
Re: NM Cable

I understand that San Francisco has limited it to ONE! I suppose they want swiss cheese lumber there.
 