N newt Senior Member Nov 4, 2004 #1 Can anyone tell me a section in the code that tells me how many nm cables allowed in bored holes.I limit the number to 3.Any ideas,thanks.
Can anyone tell me a section in the code that tells me how many nm cables allowed in bored holes.I limit the number to 3.Any ideas,thanks.
ryan_618 Senior Member Location Salt Lake City, Utah Nov 4, 2004 #2 Re: NM Cable It is not addressed. The only thing that is close is the required ampacity adjustment of the conductors if they are bundled longer than 24". See 310.15(B)(2)(a).
Re: NM Cable It is not addressed. The only thing that is close is the required ampacity adjustment of the conductors if they are bundled longer than 24". See 310.15(B)(2)(a).
electricman2 Senior Member Location North Carolina Occupation Retired Electrical Contractor Nov 4, 2004 #3 Re: NM Cable There would be a practical limit based on the width of the member and the need to maintain the required spacing from the edge.
Re: NM Cable There would be a practical limit based on the width of the member and the need to maintain the required spacing from the edge.
physis Senior Member Nov 4, 2004 #4 Re: NM Cable I understand that San Francisco has limited it to ONE! I suppose they want swiss cheese lumber there.
Re: NM Cable I understand that San Francisco has limited it to ONE! I suppose they want swiss cheese lumber there.