What does NM(Romex) fall under when identifying it (exmample:THHN,THWN)in the codebook? Do you have to derate when you bundle them up in a dwelling?
Not to split hairs here but I want you to help me by clarifying my understanding of NM.Originally posted by tom baker:
The NM conductors are rated 90 deg c, but they are not identified as THHN or similar. the cable jacket limits the ampacity to 60 Deg C
I do not realy find NM-B listed in the book334.80 Ampacity.
The ampacity of Types NM, NMC, and NMS cable shall be determined in accordance with 310.15. The ampacity shall be in accordance with the 60?C (140?F) conductor temperature rating. The 90?C (194?F) rating shall be permitted to be used for ampacity derating purposes, provided the final derated ampacity does not exceed that for a 60?C (140?F) rated conductor. The ampacity of Types NM, NMC, and NMS cable installed in cable tray shall be determined in accordance with 392.11.
Typo. Meant THW. Good catch. Thanks!Originally posted by pierre:
Wayne
Where did you find THN? <snip>
You are right. I recently saw a test of a new improved NYM cable, the German equivalent of NM. It took 36kV to break the insulation!Another belief of mine: As the insulation gets better, it gets thinner, and therefore the rating goes up. Smaller can mean better! Size does matter! I will take my answer on the air.
</font>Now - let me ask another question - and this is mainly to try to firm up my understanding of derating. Say I have eight (8) 12/2 NM cables run in a three foot (3') long nipple. Now I've gone over the 24", and I also have eight NM cables. Now, how does Table 315.10 (B)(2)(a) impact my derating.
So if instead of 8 12-2 cables, you had 4 12-3 cables in the same conduit, you'd have 8 CCC's. The neutrals are only conducting unbalanced current (310.15(B)(4)(a)).Again, one thing I'm really trying to get clear, is how the neutrals impact the derating when it comes to the Table 310.16 (B)(2)(a). Now let's specify this is a situation in a residential dwelling - so single phase 120/240.
Not sure but since you are in resi wouldn't you use Annex B Table B.310.11 for your percent of derate, since you have divers loads. So in my understanding I have 8 12/2 so 16ccc's, I could use 90degree and the above table says 70 percent.Is this correct or not? They are rated 30amp 90degree 10-24ccc's 70 percent =21amps.Originally posted by georgestolz:
So, you have 16 CCC's. You would have to derate them by 50%.
Since the requirements of 210.11 & 210.52 call for 15 and 20 amp circuits and receptacles for certain areas, if those circuits are a part of this bundled NM, you would have to upsize the conductors to maintain that rating on the handle of the circuit breaker.
(As in, you couldn't simply put a 10 amp breaker on dining room wall space receptacles, because 20 amp circuits are called for.)
So if instead of 8 12-2 cables, you had 4 12-3 cables in the same conduit, you'd have 8 CCC's. The neutrals are only conducting unbalanced current (310.15(B)(4)(a)).Again, one thing I'm really trying to get clear, is how the neutrals impact the derating when it comes to the Table 310.16 (B)(2)(a). Now let's specify this is a situation in a residential dwelling - so single phase 120/240.
You would derate by 70%.
Also, by 334.80, you can use the 90?C rating for derating purposes. By 310.16, #12 CU is good for 30 amps @ 90?C.
30 amps x 70% = 21 amps.
You can still use a 20 amp breaker for these circuits. [/qb]
Just my assumption. That's why I'm asking you.Originally posted by georgestolz:
Gern, how do you know for sure we have load diversity? Isn't that presumptive?