Re: NM Derating
[ January 23, 2006, 04:21 PM: Message edited by: iwire ]
Only if you are an engineer.Originally posted by gerns:
Not sure but since you are in resi wouldn't you use Annex B Table B.310.11 for your percent of derate, since you have divers loads.
310.15 Ampacities for Conductors Rated 0?2000 Volts.
(A) General.
(1) Tables or Engineering Supervision. Ampacities for conductors shall be permitted to be determined by tables or under engineering supervision, as provided in 310.15(B) and (C).
(B) Tables. Ampacities for conductors rated 0 to 2000 volts shall be as specified in the Allowable Ampacity Table 310.16 through Table 310.19 and Ampacity Table 310.20 through 310.23 as modified by (1) through (6).
(C) Engineering Supervision. Under engineering supervision, conductor ampacities shall be permitted to be calculated by means of the following general formula:.....
[ January 23, 2006, 04:21 PM: Message edited by: iwire ]