ramsy
NoFixNoPay Electric
- LA basin, CA
- Service Electrician
The 90C requirement for NM cable was part of the 84 NEC.
Does that mean new light fixtures are not allowed on old 14-2 cables, before 90C code was adopted?
Most residential lighting fixtures have instructions requiring 90C conductors.
Does that mean pigtails are required, and what length pigtails?
is there any procedural code reference, or OEM instruction for this?
It means the conductors in the box supplying the fixture must be rated for 90°C. I has nothing to do with pigtails. If you have 75 or 60° wires in the box, you can't "cheat" and use a 90° pigtail.
Instructions will be a part of the listing.
Is this cheating thing exclusively a listing requirement?
Or is there also code cheating reference?
.......Most of the time this is due to over lamping but having a higher temperature rated insulation goes a long way to help.
Yes, but didn't notice 90°C requirement for the new light fixture. Usually a ceiling fan or flush mount LED replacement...I take it you have never removed a ceiling fixture and seen the insulation on the branch circuit conductors burnt to a crisp? Most of the time this is due to over lamping..
........Wonder how many contractors are installing these in old buildings with 60C cables?
Do not recall ever seeing any code paragraph on use of old NM.
Got a few rolls of 250 12/2wg still in original boxes. Not stiff, no apparent ageing of insulation or covering
Any reason to not use this NM from 1982 - still had the price tag, $18.95 for 250 ft rolls.
More to the point... is there any way to verify if a cable is (or isn't) 90°C rated?
An often useful, but not foolproof, way to check is to carry a sample of each type of the wire around with you. The old 60 deg. wire often has thicker insulation on it than the 90 deg variety does. The black ( and if you look closely, the white) of 90 deg. insulation tend to be a bit shiny, the 60 deg. a dull color. Something to compare may help.