Can someone tell me if there is a code reference that does not allow NM to be run in carlon or seal tite flex for A/C connections.
Don I agree, but where does it say that in the code?Originally posted by don_resqcapt19:
Wayne,
... NM is suitable for dry locations only... Don
Section 334.10(A)(1).Originally posted by ryan_618:
Don I agree, but where does it say that in the code?Originally posted by don_resqcapt19:
Wayne,
... NM is suitable for dry locations only... Don
The 2005 code will allow NM in raceways, but it still is not permitted in wet locations. Outside raceways are wet locations and NM is not permitted. That won't change in 05 code.I really think that since it is in carlon that it would get wet and I guess the NEC Board agrees with that since they are going to allow it in 2005.
In my opinion, the interior of all raceways that are installed in wet locations is also a wet location and requires the use of cables or conductors that are listed for use in wet locations.doesn't the carflex make it a non-wet location,therefore permitting it?
Because the code says NM is not permitted in wet locations. And if the conductors are THHN, they are not suitable for wet locationsisn`t nm comprised of thhn conductors so why is this an issue?