looking at 310.13 I think romex is considered type tw. Its been a while does that sound right? If so I see the difference.
No, NM is a cable type not a conductor type. The type of conductors installed in an NM cable has to be 90 degree C rated (See 334.112). Type TW conductors are only rated at 60 degrees C so they can't be installed in NM cable anymore.
Chris