Re: NM in Liquidtite
"THHN is not for wet locations, and besides, where is this information found that the conductors in NM are THHN or any specifc insulation type"
Roger I stand corrected,I should have known that post would have come back to bite me.Yes again, you are correct since the conductors inside NM have no type printed on the insulation to say thhn is incorrect.I guess I heard it and it stuck "nm is thhn,nm is thhn,nm is thhn"
You are right I have never been tagged for it but I guess that the inspectors and myself don`t consider within LT as being in a wet location even outdoors.Because of the following.....
100 does state Wet location as being:Location underground or in concrete slabs or masonary in direct contact with earth,in locations subject to saturation with water or other liquids such as a vehicle washing areas
and in unprotected locations exposed to weather.
But, 334.12 d does say NM can`t be installed "Where exposed or subject to excessive moisture or dampness " That would hold up except that 356.10 (2) says LFNC is permitted Where protection of the contained conductors is required from vapors liquids or solids.
356.10 (3) says LFNMC is suitable for outdoor locations where listed and marked as suitable for the purpose.
So if LFNMCis listed as protection from vapors liquids or solids then the conductors within the LFNMC do not have to be rated as suitable for a wet location and the conductors that are from nm are ok to install in LFNMC.
If there is data to say otherwise let me know.