Re: NM in Liquidtite
I also agree that when LFNMC is installed outside the interior is not a wet nor even a damp location
"unless there is a dehumidifier installed on the raceway."
JW where can I find data to back that claim ?
As I see it and others may have a different view

but it is written in the book that we quote from...............................
' 100 says - Locations wet - Installations under ground or in concrete slabs or masonary in direct contact with the earth; in locations subject to saturation with water or other liquids,such as vehicle washing areas; and in unprotected locations exposed to weather.
334.12 10 (d)Where exposed to excessive moisture or dampness. (OK so this we already know)
356.6 - Says LFNC and associated fittings shall be listed.
And when you bring 356.10 (2) into the picture - Where protection of the contained conductors is required from VAPORS LIQUIDS or solids.
All these related articles tell me that when using LFNC it keeps water out and the listed associated fittings are keeping water out. There is no mention of condensation anywhere in this area we are reffering to .So IMO as I interpet these articles , the conductors inside a piece of LFNC DO NOT have to be listed as suitable for use in a wet location.
(quote) THHN is not for wet locations, and besides, where is this information found that the conductors in NM are THHN or any specifc insulation type (quote)
You are correct Roger THHN is not for wet locations but inside LFNC is not a wet location.As far as conductors in NM I assumed that since NM is not listed for a wet location they are THHN ( my mistake to assume since we can`t tell what they are without them being marked )
(quote)When it is raining the humidity is at 100% inside and outside the liquid tight flexible nonmetallic conduit unless there is a dehumidifier installed on the raceway.
100% humidity equates to dampness
There is no reference to humidity inside or outside a piece of LFNC anywhere as far as I can see.There are referances to water,moisture but not humidity.
To use your theory then if we wire a home in NM and use a 3R panel that is mounted on the exterior of a home the conductors that terminate in that panel can`t be NM