NM in same holes as water pipes

Status
Not open for further replies.
I was in a building today in which I observed NM that had been run horizontally through the same holes in floor joists as a gavanized cold water pipe. While the holes were big enough to hold both, I told the owner that this was not good workmanship and might be a Code violation. But now that I've scanned my NEC I can't actually find anything that prohibits it. Is there a clearance requirement or a requirement for separate penetrations, and if so where is it?
 
I agree with Bob, and in some cases it may be better than making Swiss cheese out of the floor joist.
 
winnie said:
If there is sufficient condensation on the cold water pipe (sweating), then would this be considered a wet location?

-Jon

Now that's a different outlook. I would think if there was that much sweating we would have a water problem. But I also would never use the same hole as the water pipe. One reason is that the plumbers around here drill a hole the size of their pipe, you could never get a wire in there.
 
winnie said:
If there is sufficient condensation on the cold water pipe (sweating), then would this be considered a wet location?

-Jon
Location, Wet. Installations under ground or in concrete
slabs or masonry in direct contact with the earth; in locations
subject to saturation with water or other liquids, such
as vehicle washing areas; and in unprotected locations exposed
to weather.

The answer by the very defintion of wet location is NO!
 
I would not do it, but then.

Water hammer could be an issue, moving water pipes, rubbing the NM against the studs.

Hot water could be an issue.

But then the only time we use NM is in emergency situations for power and or light.
 