First off, with 14-10 AWG conductors anyway, you need to have more than 9 current carrying conductors in said "bundle" before ampacity adjustments may make you increase conductor size.I never staple more than two cables together due to bundling concerns. (I'm concerned the inspector will think it's bundling and make me redo it.) For three or more cables I use a stacker.
I also don't use regular metal staples because I'm concerned about accidentally shorting the conductors. This is something you would not notice until much later, possibly after the drywall is up. I always use staples with a plastic top or a plastic insulator. Paying the labor to locate one short would totally wipe out any savings from using cheap metal staples. (Probably years worth of savings.)
Is that for me? MaybeProbably not if your inspector uses a tape measure.![]()
Those are 2X6's?Is that for me? Maybe
Here's a couple of pics to show what I mean.
I don't have any pics with 2x4s but it measures fine
He addressed that. Still would be able to center same cables down a 2x4 and keep out of the 1-1/4 no go zone at the edges though there is little room for errors.Those are 2X6's?
Where does the nonsense end though? lots of listed things get used for something they are not listed for. Code specifically calls out things it requires to be listed also.Although I agree Staples are not required to be listed, if they do provide instructions on the box as far as number of cables I think you are bound to it by 110.3 B