Jersey
Enclosed are two plastic boxes. One has the entry with a piece of plastic that can be knocked out and one has a entry that is more like a squeeze connector.
Can both types support of nm at 12" or would the plastic knock out type need to be 8" away? Thank you
 

Attachments

  • box 1.png
    box 1.png
    174.5 KB · Views: 4
  • box 2.png
    box 2.png
    219 KB · Views: 4
334.30 Securing and Supporting.

Nonmetallic-sheathed cable shall be supported and secured by staples, cable ties listed and identified for securement and support, or straps, hangers, or similar fittings designed and installed so as not to damage the cable, at intervals not exceeding 1.4 m (41⁄2 ft) and within 300 mm (12 in.) of every cable entry into enclosures such as outlet boxes, junction boxes, cabinets, or fittings. The cable length between the cable entry and the closest cable support shall not exceed 450 mm (18 in.). Flat cables shall not be stapled on edge.

314.17 Conductors and Cables Entering Boxes, Conduit Bodies, or Fittings


Exception: Where nonmetallic-sheathed cable is used with single gang nonmetallic boxes not larger than a nominal size 57 mm × 100 mm (21⁄4 in. × 4 in.) mounted in walls or ceilings, and where the cable is fastened within 200 mm (8 in.) of the box measured along the sheath and where the sheath extends through a cable knockout not less than 6 mm (1⁄4 in.), securing the cable to the box shall not be required. Multiple cable entries shall be permitted in a single cable knockout opening.
 