Nm/uf inconduit?

Status
Not open for further replies.

WAR EAGLE

Member
Location
S.E.Michigan
Thanks alot guys, never saw that note 9 in ch.9 ,thats all the ammo I need.
Oh and celtic so far it has just been a discusion, tomorrow i'll lay the wager out and see if he takes the bait.
 

celtic

Senior Member
Location
NJ
Go for it War....if you want to get a steak dinner out of him, let him "win" the "first bet"...then double-or-nothing for the steak ~ the "real" bet ;)
 

allenwayne

Senior Member
Dennis you posted not outside.That is not always the case NM can`t be used in conduit under ground .Like in a slab so it is not allowed there.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
allenwayne said:
Dennis you posted not outside.That is not always the case NM can`t be used in conduit under ground .Like in a slab so it is not allowed there.
IMO, and also around here it cannot be installed in carflex to an A/c unit. Once it leaves the house structure many consider it outside and must have a wet location label on it. Since NM does not have any markings on its conductors or jacket we must assume it is not rated for outdoor use.

I didn't say I agree with it but that is how I understand it.

edited-- we had a thread on this awile ago.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
If you piped PVC around the outside of a house would you run THHN or TW/THHWN (something with a W in it). Outside is wet location whether it is in conduit or not. NM is not rated for wet location.
 

blue spark

Senior Member
Location
MN
allenwayne said:
Dennis you posted not outside.That is not always the case NM can`t be used in conduit under ground .Like in a slab so it is not allowed there.
If the slab is on grade you can. Below grade, nope.
 

celtic

Senior Member
Location
NJ
(From Dec 1, 1995..EC&M)

1. If four 12-2 Type NM cables measuring 0.48 in. by 0.20 in. in cross section are run in a raceway along a wall 70 ft between. two pull boxes, what size raceway must be installed? The cross-sectional area of the cable is 0.075 [in.sup.2].

a. 1-in.
b. 1 1/4-in.
c. 1 1/2-in.
d. 2-in

[ Tables, examples, and appendices - chapter 9 and appendix B]
Dec 1, 1995 12:00 PM, Hartwell, Frederic P.

The above question and a variation or two are answered in the link....today's NEC may be slightly different, but the same principles are followed.
 