mwm1752
- Aspen, Colo
your engineer used code references that would apply to type of construction --
(A) Types NM, NMC, and NMS. Types NM, NMC, and NMS cables shall not be permitted as follows:
(1) In any dwelling or structure not specifically permitted in 334.10(1), (2), (3), and (5)
334.10 Uses Permitted
Type NM, Type NMC, and Type NMS cables shall be permitted to be used in t he following, except as prohibited in 334.12:
(1)One- and two-family dwellings and their attached or detached garages, and their storage buildings. Not Applicable to situation
(2) Multi-family dwellings permitted to be of Types III, IV, and V construction. Not Applicable to situation
(3) Other structures permitted to be of Types III, IV, and V construction. Cables shall be concealed within walls, floors, or ceilings that provide a thermal barrier of material that has at least a 15-minute finish rating as identified in listings of fire-rated assemblies. Only applies to specific area’s not type of construction
(5) Types I and II construction where installed within raceways permitted to be installed in Types I and II construction. Still can use NM in a raceway.
Certianly sounds confusing -- were the code sections the engineer stated recieved by the building dept plan review? Do not know about CEC