see post #14Better yet show him Article 314.17(C) Exception (Last line of) "Multiple cable entries shall be permitted in a single cable knockout opening"
see post #14Better yet show him Article 314.17(C) Exception (Last line of) "Multiple cable entries shall be permitted in a single cable knockout opening"
Single gang box is ok if secured within 8" of box, not for multi gang.
Hate those Carlon boxes.
Some do - some don't. The ones on this do... (Most do...)Care to explain this?
Multi-gang Carlon boxes do not have internal clamps either.
Ref: http://www.carlon.com/FAQs/FAQ-ZipBoxes.pdfHow many cables can you put in one integral cable clamp?
One. The National Electrical Code section 314.17(c) Exception allows you to put multiple cables through a knockout, but only one is allowed through each clamp.
Gotta read the whole Exception. The last sentence does not stand alone.314.17(C) ex says "single entry" not single gang
2008 NEC
314.17(C) Exception: Where nonmetallic-sheathed cable or multiconductor Type UF cable is used with single gang boxes not larger than a nominal size 57 mm ? 100 mm (21/4 in. ? 4 in.) mounted in walls or ceilings, and where the cable is fastened within 200 mm (8 in.) of the box measured along the sheath and where the sheath extends through a cable knockout not less than 6 mm (1/4 in.), securing the cable to the box shall not be required. Multiple cable entries shall be permitted in a single cable knockout opening.
Yep. The clamps in multi-gang boxes work well with stackers, which don't grip.I've always stapled within 8" with a plastic box regardless. I had not realized that the plastic tabs are considered a clamp.
You also don't have to staple cables run through horizontal holes and enter boxes if they're close enough.
millieamp said:But, what the hell, I ended up redoing the work. Sometimes you just have to bend over and take it.
Ya, the 2008 Handbook Exhibit 314.5 is new (it wasn't in the '05). The '08 Exhibit 314.5 shows an 18 cubic inch blue nail-on single gang wall box (Carlon B118A) that has the square knockouts, and two NM-B cables go thru one knockout.My handbook is the '05 edition and Exhibit 314.5 is about a flexible surface extension from a flush-mounted box.
Perhaps you missed the links in E57's Post #23.Thanks for the support, people. I emailed Carlon and they didn't reply (yet?). . . If the issue is securing the cables tightly, then the 8" staple rule would seem to apply, but what do I know? If the issue is tearing the insulation, I could see it as a concern but I really do need to hear from Carlon (Lamson and Sessions).
An inspector told me that it's a code violation to put the NM cable in the opening closest to the stud of a single gang nail on box. Why?
An inspector told me that it's a code violation to put the NM cable in the opening closest to the stud of a single gang nail on box. Why?
As an interesting side note - 08 Exhibit 314.5 - I have been called out by inspectors for using the first knock out on 2X4 frameing. Two wires in one knock out was OK but needed to use the knock out farthest away from stud.
The 1 1/4" rule for protection from rock screws.
300.4(d) 1 1/4" from face of stud.
Yeah. I've had that too, here in the Twin Cities.As an interesting side note - 08 Exhibit 314.5 - I have been called out by inspectors for using the first knock out on 2X4 frameing. Two wires in one knock out was OK but needed to use the knock out farthest away from stud.
The 1 1/4" rule for protection from rock screws.