Oh I noticed, I just did not want to pick on you I have to wait till Saturday for that.Originally posted by physis:
Oh man, Bob didn't notice yet.
Yes, no, maybeOriginally posted by physis:
Ok, fair enough.
Except I got caught in this derating term too, you mean correction factor?
Crankshaft I am sure that is what someone told you. However please follow this link that Roger posted.Originally posted by crankshaft:
the -b means the non metallic sheathed cable comes with a bare or insulated ground. nm is a flat 2 conductor cable. nm-b is a 3 conductor cable
The B has nothing to do with bare, insulated, round, flat or number of conductors.The "B" denotes that individual conductor insulation is rated 90?C; however, ampacity is limited to that for a 60?C conductor (see NEC Section 336-26, 1999 edition). Thermoplastic (PVC) conductor insulation-nylon jacketed, with overall PVC cable jacket.