I am suppling a new 480 service to a pump house building and I was going to install 2 ground rods for the new service. I am also installing a transformer to the building for 120 needs. There is no building steel so my question is do I just tie the waterpipe and ground rod together NEC 250.50 or do I use the waterpipe for the transformer grounding 250.104(D)(1). Or do they all get tied together?
There is also another detached building that we are suppling a 480 panel (from the first building) and another transformer for 120 needs. I am assuming that building needs its own grounding system (2 ground rods), but I had the same question about the transformer grounding.
Thank you