Hi all!
I recently found this site and see some very knowledgeable people post here. I?ve been looking for a site like this for some sound advice on a project I?ve been working on where I?ve been getting conflicting answers.
Here?s the scenario:
I?ve been asked to put into service a 200 amp sub-panel off of a 150kw generator that has it?s own structure that also houses the main disconnect, main panel and automatic transfer switch. The system is setup non SDS , (does not switch neutral) and 120/208V 3ph.
The neutral on the generator is not bonded to generator frame.
The sub-panel is in a separate building located about 50yds away that was installed but never was put into service about 15 years ago. It is a 200A, 3ph panel..
Here?s the problem:
When I opened the panel, I discovered that there were 3 phase conductors, 1 neutral but no EGC conductor. The conductors are directly buried in the ground from the generator building to the sub-panel building, so pulling in an EGC is out of the question. I thought about just wiring this panel single phase and using one of the phase conductors as the EGC. This would not be much of a problem, as there is only going to be a small load on this panel, but it would leave 1/3 of the panel dead.
I consulted with others on this problem and was told I could just re-ground the neutral with the equipment ground in this panel just like a new service as long as there are no conductive metallic paths between the two buildings. Then I was told I couldn?t do this because since the neutral is not being switched, it is necessary to install an EGC conductor.
There is yet another 1ph 100A sub-panel being fed from this 200A sub-panel going to another building that was not supplied with an EGC. This is a main lug panel that I assume will have to be replaced with a main breaker panel.
I?ve have tried to provide as many details as possible but if any other info. is needed please ask.
All comments, opinions and advice will be greatly appreciated as I need to get started on this soon.
I recently found this site and see some very knowledgeable people post here. I?ve been looking for a site like this for some sound advice on a project I?ve been working on where I?ve been getting conflicting answers.
Here?s the scenario:
I?ve been asked to put into service a 200 amp sub-panel off of a 150kw generator that has it?s own structure that also houses the main disconnect, main panel and automatic transfer switch. The system is setup non SDS , (does not switch neutral) and 120/208V 3ph.
The neutral on the generator is not bonded to generator frame.
The sub-panel is in a separate building located about 50yds away that was installed but never was put into service about 15 years ago. It is a 200A, 3ph panel..
Here?s the problem:
When I opened the panel, I discovered that there were 3 phase conductors, 1 neutral but no EGC conductor. The conductors are directly buried in the ground from the generator building to the sub-panel building, so pulling in an EGC is out of the question. I thought about just wiring this panel single phase and using one of the phase conductors as the EGC. This would not be much of a problem, as there is only going to be a small load on this panel, but it would leave 1/3 of the panel dead.
I consulted with others on this problem and was told I could just re-ground the neutral with the equipment ground in this panel just like a new service as long as there are no conductive metallic paths between the two buildings. Then I was told I couldn?t do this because since the neutral is not being switched, it is necessary to install an EGC conductor.
There is yet another 1ph 100A sub-panel being fed from this 200A sub-panel going to another building that was not supplied with an EGC. This is a main lug panel that I assume will have to be replaced with a main breaker panel.
I?ve have tried to provide as many details as possible but if any other info. is needed please ask.
All comments, opinions and advice will be greatly appreciated as I need to get started on this soon.