As it is, yes, it's safe. As has been said, it's the same as every residential service.I still want to know if this is a "safe" set-up. What are the potential hazards here and why did they change the code?
Correctamundo.If the neutrals and grounds are bonded, essentially the neutral is used as the EGC? Correct?
Yes, because (presuming the neutral is what you leave connected) a short from a hot to what should be grounded will energize what would otherwise be bonded and trip a breakerIf the neutrals and grounds were separated in sub and still had no equip ground, this poses danger? Correct?
As I mentioned earlier, it's like the past allowance for 3-wire major appliance circuits that may remain, while new installations require the 4-wire circuit. Many code rules evolve because of events that occur over time that cause reconsideration of past rules.I am pretty sure pulling the EGC won't be that bad, we will do this at no charge. But I want to understand electrically what is going on, and why some situations are safe and some not, and why the code would change.
I had a customer whose son was severely shocked because the neutral of their 3-wire-supplied range became disconnected in the range's wiring compartment, and he contacted the range and the sink simultaneously. They had noticed that the clock and light stopped working, but those still energized the range cabinet.