Re: No Good Options
Originally posted by jimwalker:
With load off i see no danger in pulling a meter.The neutral stays in tack its only the 2 hots being removed.
Jim apparently electric equipment never malfunctions in Florida? :roll:
How the meter persons do their job has nothing to do with us as electrical contractors.
Originally posted by jimwalker:
Yes the legality is an issue.As long as it's done by an electrician for the purpose of repairs,inspection,replacement of main breaker,etc. then they should have no problem with this.
Jim you are in FPL's territory correct?
If so what you just posted is not accurate.
Right from FPL's Green Book to you here.
The green book is available on line as a .pdf at
www.fpl.com
III.H. Unauthorized Connections & Disconnections
All connections of the Customer's wiring to that of FPL, all disconnects of service entrance conductors, all meter removals and installations and all breaking of FPL meter equipment seals shall be made only by FPL, except as allowed in Section III.I of these standards.
Any other connection or disconnection of FPL's service by the Customer or his agent is prohibited. If done with the intent to injure or defraud, it is punishable by law. Violators will be prosecuted.
So the basic rule is no one except FPL employees can ever break a seal.
Section III.I does provide an exception specifically for service changes only, not repair work.
III.I. Change in Service Requirements (Service Changes)
The Customer will normally own all the service facilities on his side of the point of delivery; i.e., the point where FPL's wires carrying the voltage of supply are to join the Customer's wires, except for the meters which will be owned by FPL.
The Customer shall notify FPL, in advance, when a change in service (service change) is being considered to accommodate provisions that service and metering facilities remain adequate.
When a service change requires disconnection of FPL's service, the customer shall request a disconnect/reconnect from FPL. The Customer shall establish an advance appointment to ensure proper coordination between his electrical contractor and FPL crews who will disconnect the service and later reconnect after an inspection when required by local authorities) is received.
Now here is the exception that allows an EC under certain circumstances to disconnect power.
Exception:
FPL normally performs both the disconnect and reconnect. In certain cases however, the Customer's licensed and qualified electrical contractor is allowed, at his option, but only when approved by FPL, to perform the disconnect on overhead services only, when the following criteria are met:
</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">- The Customer shall be a residential or small commercial facility with a main line switch rating of 300 Amps or less, served by an FPL single phase overhead service. No three phase service shall be disconnected by an electrical contractor. FPL must disconnect all three phase services to ensure that proper phase rotation is maintained.</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">- FPL service attachment point at the building or structure shall remain intact. No service shall be removed from the attachment point or the attachment point altered in any way.</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">- The meter socket(s) must not have an FPL locking device installed.</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">- If multiple meters are involved, the electrician shall "mark" each meter and socket.</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">- Only a licensed and qualified electrical contractor may perform the disconnect function and he shall schedule a reconnect date appointment) with FPL before disconnecting the service. If the appointment is not made before the disconnect, FPL will not be responsible for a same day reconnect.</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">- The service shall be cut on the load side of FPL's connection to the customer's service conductors. No FPL conductors are to be cut.</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">- The service shall be disconnected before removing the meter(s). No meter is to be removed from an energized meter socket.</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">- FPL personnel only are to perform the reconnect and only after an inspection (if required by the local authority) is received. Electrical contractors are not allowed to reconnect the service.</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">- The decision to perform this type of disconnect is entirely voluntary for the electrical contractor and allows work to commence without having to wait for FPL to disconnect the service. However, the electrical contractor still has the option of FPL performing the disconnect if he prefers.</font>
<font size="2" face="Verdana, Helvetica, sans-serif">
Please notice:
"No meter is to be removed from an energized meter socket"
Jim I am not a fool, these rule most likely do get broken.
That said I think you are wrong to get on this forum and basically tell all the members here that braking the rules is fine there is no danger and that the power company will have no problem with any of it.
Originally posted by jimwalker:
On a service call i often have seen panels with buss bars that are ready to arc over any minute.They might last a few more days or weeks ,then again maybe only hours.
If in your judgment it is that bad and the POCO is not responsive call the FD and tell them the situation.
Originally posted by jimwalker:
The cost is high enough without adding extra trips or causing them to move out for a couple days and lose all the food in frig.
OK, now I understand we all should risk getting burned so that tonights steak is not ruined. :roll:
Originally posted by jimwalker:
Lets see how far they get in court with keeping customer from working on there own equipment.Yes meter is poco property and i am not stealing it or altering it in any way,nor am i stealing electric.
Jim forget about the stealing, if as you replace the meter and it shorts out you and your company will be held liable for all damages as you where never authorized to restore power.
Bottom line Jim in my opinion you are giving out dangerous advice here and I hope you rethink your posts and your work practices.
Bob