On a existing 100 amp service over head built with RMC. with no grounding electrode. can I add a ground rod and bond the grounding electrode conductor to the RMC with a ul approved brass two piece ground clamp. per 2011 code?
I’m sorry but why now grounding electrode?
Sent from my iPad using Tapatalk
On a existing 100 amp service over head built with RMC. with no grounding electrode. can I add a ground rod and bond the grounding electrode conductor to the RMC with a ul approved brass two piece ground clamp. per 2011 code?
You can either connect it to the main panel, meter base enclosure or the neutral at the overhead drop