It was presented to me that prior to 2008 a ground was not required to be brought to a detached structure when bringing out a feeder
Only two hots and the neutral
Is this true. I don't remember that.
Thank you
Equipment grounding conductor.
I used that exception all the time to save those installing a manufactured home from having to use a 4-wire system when the disconnect was on a pole or if they built a barn first and feed the home from the meter on the barn.
Thank you for the responses.
Would that exception not have worked because part of that exemption mentioned no grounded metal ?
And I would think prefabed homes have grounded metal ( or well at that time before all these plastic systems )
:?Equipment grounding conductor.
I used that exception all the time to save those installing a manufactured home from having to use a 4-wire system when the disconnect was on a pole or if they built a barn first and feed the home from the meter on the barn.
:?
Manufactured homes are (and have been for a long time) permitted to have service equipment installed in/on the home. They never absolutely required a 4 wire supply until 2008 when all separate structures required a separate EGC.
Mobile homes have always required a 4 wire feeder from the service disconnect or when not supplied by a service a service rated disconnect. Even before 2008 this service rated disconnect could have been supplied with only a three wire feeder, but the individual feeder to the home itself had to be 4 wire.
Ok an anchoring system like you provided a link to is the main difference here. I never see manufactured homes that are not on a permanent foundation, then again maybe I just assumed some manufactured homes were mobile homes.You are partially correct.
Here is why the 4-wire would have been required:
550.32 Service Equipment.
(A) Mobile Home Service Equipment. The mobile home
service equipment shall be located adjacent to the mobile
home and not mounted in or on the mobile home. The
service equipment shall be located in sight from and not
more than 9.0 m (30 ft) from the exterior wall of the mobile
home it serves. The service equipment shall be permitted to
be located elsewhere on the premises, provided that a disconnecting
means suitable for use as service equipment islocated within sight from and not more than 9.0 m (30 ft)
from the exterior wall of the mobile home it serves and is
rated not less than that required for service equipment in
accordance with 550.32(C). Grounding at the disconnecting
means shall be in accordance with 250.32.
This is what most installers did because they did not go to the next:
(B) Manufactured Home Service Equipment. The manufactured
home service equipment shall be permitted to be
installed in or on a manufactured home, provided that all of
the following conditions are met:
You can STILL use a 3-wire to the manufactured home.
Example:
Meter on the home or a pole or wherever.
Run the 3-wire underground (outside the structure) concrete slab or not, up out of the 'ground' and straight up into the factory installed panel.
Now you will have to 'bond' inside the panel.
Now it gets better. This is a permanent install.
http://www.tiedown.com/pdf/d552.pdf
I have been asking the same question since the 90's. I can only figure that it has to do with the way our power grid is set up. Somebody or some group set out to change the entire US but only managed to get as far as the rules for inside wire men.In electrical terms, how is a second building different from the service? Why do the electrons behave differently on the load side of the service? Either both the service and the second building feeder are safe using the grounded conductor as both the grounded and grounding conductor or neither one is safe unless you install an EGC. There is no way that one requires an EGC for safety and the other doesn't, other than the code rule.
Ok an anchoring system like you provided a link to is the main difference here. I never see manufactured homes that are not on a permanent foundation, then again maybe I just assumed some manufactured homes were mobile homes.
Other situation that usually comes up is if the panel is not at an exterior wall you will be running a feeder with separate EGC to it anyway because of 230.70(A)(1), unless you have an AHJ that is pretty relaxed on how far service conductors can enter a building.
Many homes will not have a panel in an exterior wall because of thermal insulation issues created if it is in an external wall.
I have been asking the same question since the 90's. I can only figure that it has to do with the way our power grid is set up. Somebody or some group set out to change the entire US but only managed to get as far as the rules for inside wire men.
In electrical terms, how is a second building different from the service? Why do the electrons behave differently on the load side of the service? Either both the service and the second building feeder are safe using the grounded conductor as both the grounded and grounding conductor or neither one is safe unless you install an EGC. There is no way that one requires an EGC for safety and the other doesn't, other than the code rule.
Augie,In the 2008 ROPs there are many proposals on this including 5-119 Log 2395 submitted by Mike Holt.
In substantiating the change requiring the EGC between buildings the prime reason, if I read correctly, is the dangers, both fire and shock, that occur when you end up with an alternate path (communication cables, piping, etc). Although the Code panels normally don't address "what ifs", the high probability of a system being installed after the electrical that would allow such a path was found to warrant the requirement.
The CMP followed the thinking that accompanied the earlier requirement for ranges and clothes dryers.
Augie,
My problem is that the second building is electrically no different from a service and not only are parallel paths not prohibited at services, they are actually required by the code rules.