Dennis, I am not aware of any residential use 120/240 volt dryer that cannot be used with a 3 wire cord.
250.140 does not allow this if there is a grounding conductor present in the outlet.
Dennis, I am not aware of any residential use 120/240 volt dryer that cannot be used with a 3 wire cord.
That is correct. The dryer can be used on either type of existing ciruit. You would match the cord to the circuit. Of course if you are installing a new circuit it would have to include both a grounded and grounding conductor.250.140 does not allow this if there is a grounding conductor present in the outlet.
It is a parallel circuit...the voltage is the same across the impedances that are in parallel. If the frame of the equipment is energized and in contact with the earth, the person is in parallel with the frame of the equipment....
Maybe this is my problem I am thinking of it as a voltage divider. But in essence wont the voltage across your body be determined by a voltage divider setup by impedances, with the intentional bond to ground creating a parallel low impedacne with body? ...
Yes, which is exactly why they decided to require a separate grounding conductor. If a neutral opens, the load side of that open conductor will no longer be at, or close to the supply's neutral voltage, which should be at, or close to zero volts.Yes but what if you intentionally bond the dryer frame to ground. Wont the low impedance of this intnetional bond create a parallel low impedance with the body thus dropping the majority of the voltage elsewhere?
Yes, that is correct. They stopped the allowance for the neutral to double as the EGC is to prevent the hazard of energized surfaces when the supply neutral is lost.Maybe this is my problem I am thinking of it as a voltage divider. But in essence wont the voltage across your body be determined by a voltage divider setup by impedances, with the intentional bond to ground creating a parallel low impedacne with body?
I believe so. When that happens, only the earthen pathway between the source's electrode and the load's electrode remains, and is generally very bad at it. In cities with a metal water supply, one house's neutral is tied to the neighbors' neutrals, so they seem to function okay, at least until a water meter is removed.Am I right in understanding your explanation as to what happens when you loose a neutral on the line side of the main bonding jumper?
Larry, are you saying if the dryer's frame is grounded thru the neutral conductor, and you loose that neutral anywhere, the frame automatically becomes energized?
To expand on Bob's response, anything on the load side of the break can become energized, because of a combination of the equipment enclosure being tied to the neutral and current through any line-to-neutral part of the load.Larry, are you saying if the dryer's frame is grounded thru the neutral conductor, and you loose that neutral anywhere, the frame automatically becomes energized?
...
So, the literal answer to your questions is "Yes, any time the dryer is on, so there is a path between an energized conductor and the now-energized appliance cabinet through part of the load."
True, although our dryer has no bulb, so I didn't think about it.Actually the dryer wouldn't even have to be on to energize the frame if the neutral were lost line-side. It would be enough to open the door and send power to the light bulb.
Why after so many years of it being OK for the neutral to be connected to the frame, it's now a violation? Where people getting shocked?
I thought that older dryers didn't have a need for a neutral. That both the heating element and the motor were 220V. Now they have electronics and timers and other stuff that uses the neutral.
In response to both of these posts, it was always two hots and the neutral, which was permitted to do bonding tasks in the past.when was a kid we ran 3 wire dryers then some time in the 90's in changed to 4 wire
Same with the range, it was 2 hots and a ground, ran timer, light, ect.
To expand on Bob's response, anything on the load side of the break can become energized, because of a combination of the equipment enclosure being tied to the neutral and current through any line-to-neutral part of the load.
It's the exact same thing as an open neutral to a service. Unless the two opposing line-to-neutral loads happen to match, the voltage on the normally-zero-volts-to-earth neutral rises. In the house, we see it as a voltage imbalance.
However, to the outside world, the entrire house's "ground plane" becomes energized. We don't notice that because we're inside the "box", but outside, the normally-grounded surfaces, such as the meter base and water taps, are hot.
So, whether the dryer's cabinet is a shock hazard depends on whether you're inside the box (or the house), where you're safe, or outside the box (or the dryer), standing on a concrete floor. Remember, it's not voltage that zaps, it's current.
So, the literal answer to your questions is "Yes, any time the dryer is on, so there is a path between an energized conductor and the now-energized appliance cabinet through part of the load."
On MY dryer, the drum lamp is 120V connected, I ASSUME, from phase to neutral. If neutral is also frame ground, the frame will have 120 to (cold water pipe or washer frame?) through the lamp filament.Just so I understand, The frame has no EGC connected to it. It has the neutral connected to it. You lose that neutral connection, so now you have nothing grounding the frame. Why would there be any electricity on the frame? Is it like a car, where the frame is being used as a conductor for neutral current? Where not talking about some loose hot wire that just happens to be touching the frame are we? Bare with me, I'm not the sharpest tool in the shed.![]()
Because the dryer has line-to-neutral loads within it. Every dryer I've seen only powers the heating element from line-to-line; everything else is powered line-to-neutral.Just so I understand, The frame has no EGC connected to it. It has the neutral connected to it. You lose that neutral connection, so now you have nothing grounding the frame. Why would there be any electricity on the frame?
No, although that would be a hazard with an open neutral/EGC as well, because the loss of the neutral menas the loss of grounding. The cabinet is energized wither way.Is it like a car, where the frame is being used as a conductor for neutral current? Where not talking about some loose hot wire that just happens to be touching the frame are we?