Assuming no conductive paths between the two building other than the feeder circuit conductors, grounding electrodes, grounding electrode conductors and grounded to grounding bonding is required at both locations.
Even if there are conductive paths, I would put the bond in at the second building on a system with no EGC run with the feeder conductors. Without the bond you have no fault clearing path, but with it, you have a parallel path for the grounded conductor current, however that same parallel path is not only permitted but required by the code with services to multiple buildings in many cases. These paths would be a metal underground water piping sytem that is common to multiple buildings, a TV cable installation or a underground phone line line installation. In each of these cases some of the grounded conductor current will flow on the parallel path, and in the case of the common metal underground water piping system, it would not be uncommon to find 20% or more of the grounded conductor current flowing on the water pipe.
Even if there are conductive paths, I would put the bond in at the second building on a system with no EGC run with the feeder conductors. Without the bond you have no fault clearing path, but with it, you have a parallel path for the grounded conductor current, however that same parallel path is not only permitted but required by the code with services to multiple buildings in many cases. These paths would be a metal underground water piping sytem that is common to multiple buildings, a TV cable installation or a underground phone line line installation. In each of these cases some of the grounded conductor current will flow on the parallel path, and in the case of the common metal underground water piping system, it would not be uncommon to find 20% or more of the grounded conductor current flowing on the water pipe.