Phil,
Are you sure? I thought I have heard frequently that a reverse fed transformer can have a higher than normal inrush as it may not be designed to be fed from that end. You disagree?
ElectroFelon… You were too impatient.
The answer is yes… but only if it’s an emergency, AND, the Xfmr mfgr agrees! Many factors are involved. For simplicity consider an unloaded 2-winding, single-phase xfmr! Then, some of the factors to consider are:
1) Condition of the supply-side source! Should be sinusoidal, and not have significant harmonics!
2) Number of terms of the winding being energized, i.e., Np or Ns, and not turns-ratio, Np/Ns!
3) Effective impedance of the connection between the source and the winding!
4) Effective resistance of the winding being energized should not be too large relative to the induced voltage expected in that winding!
GoldDigger…
Maybe… but, still depends on the Xfmr’s parameters! Not some Rule-of-Thumb (RoT)!
Phil