Here is a GE paper on backfed inrush. The example they use is a 75kva, 480D,208Y
max inrush forward fed - 11X
max inrush reverse fed - 37X
as mentioned by iwire and templdl:
The taps are on the wrong side to correct for overvoltage. If the primary voltage is high, setting the taps down will lower the output voltage but leaves the transformer prone to over-fluxing (careful with the pronunciation, please), increasing magnetizing current - it will run hot.
And from Bes:
The paper discusses compensated windings, "Some manufacturers also build larger transformers with compensated windings." But they don't identify any culprits. I've never seen one (larger than 3kva compensated), but apparently they are out there.
Interestingly the paper does not discuss ground detectors. The only method discussed is corner grounding.
ice