Interesting aside:
Has anyone ever seen anything on minimum inrush (normal install forward feed)?
Had an occasion to advise on a temp power install. 225kva, 408D/208Y, fed with a 100A CB. Normal loading (primary side) was 50A.
I figured it would be more likely than not to trip. IEEE says 1 in 6 times the inrush will be max. All we had for instrumentation was a peak reading fluke clamp-on. That thing just oozed on line. As I recall, the inrush was less than 100A.
Considering 1 in 6 is max inrush, is 1 in 6 min inrush and the rest are scattered in between? Anybody seen any actual test results, or papers on tests?
Plenty of papers on max inrush. Haven't ever seen one on min inrush.
ice