METLABS is a NRTL. That unit apears to be military. I would use #4 and an 80 amp OCPD. The tag calls for 5 wires.
Is that unit listed for use in the US?
yes made in the USA 208 volt 60 HZ. I would like to know if I'm caculating this correctly.
Dbronx;13 the high LRA confuing. .......... this is where I loose it the LRA is 156 = in rush said:You need not bother about LRA,IMO.The protective device with MOP you calculated from RLA might be able to withstand the LRA.But check with the manufacturer for the size and type (fuse or breaker) of the protective device,anyway.
Again my limited posting has got the best of me, MANY THANK to every one who relpyed. I'll try to phone the manufacture and get back to you, I would like to shed some light on this subject for everyone interested. You referenced RLA but FLA was on the name plate I thought FLA was a larger value than RLA.You need not bother about LRA,IMO.The protective device with MOP you calculated from RLA might be able to withstand the LRA.But check with the manufacturer for the size and type (fuse or breaker) of the protective device,anyway.
Again my limited posting has got the best of me, MANY THANK to every one who relpyed. I'll try to phone the manufacture and get back to you, I would like to shed some light on this subject for everyone interested. You referenced RLA but FLA was on the name plate I thought FLA was a larger value than RLA.