The name plate stetes 208 volts, 3 phase, 60 HZ FLA 37.8, LRA 156, the high LRA confuing. I figured 37.8 FLA could ues the for conductor sizing, 37.8 X 1.25 = 47.25 for conductor size 4 awg. 37.8 X 2.25 = 85.05 amps for overcurrent Device. this is where I loose it the LRA is 156 = in rush, should LRA be used for MOP??