winnie
Senior Member
- Location
- Springfield, MA, USA
- Occupation
- Electric motor research
As I understand the original post, the utility provides 480/277V wye service.
The loads are 480V HVAC, 480V sewer pump, a 480V : 208/120V transformer, and 2 480/277V panels serving L-N loads.
A neutral conductor is required from the source to power the L-N loads. I suspect that the original installation used a single conductor for both neutral and EGC, possibility not code compliant.
Jonathan
The loads are 480V HVAC, 480V sewer pump, a 480V : 208/120V transformer, and 2 480/277V panels serving L-N loads.
A neutral conductor is required from the source to power the L-N loads. I suspect that the original installation used a single conductor for both neutral and EGC, possibility not code compliant.
Jonathan