LarryFine
Master Electrician Electric Contractor Richmond VA
- Location
- Henrico County, VA
- Occupation
- Electrical Contractor
I am proposing to upgrade a residential service by adding a second 200a panel that will be used only to supply a tankless water heater that uses four 40a circuits. The service has an exterior main disconnect next to the meter, so we're talking about a 400/320a meter base and a second 200a disconnect.
Just want to confirm that I can use SE and not SER, the neutral gets bonded/grounded in the new disconnect, and need go no farther. But, I do need to add GECs to the new disconnect, and cannot depend on the existing ones in the present disconnect, right?
Just want to confirm that I can use SE and not SER, the neutral gets bonded/grounded in the new disconnect, and need go no farther. But, I do need to add GECs to the new disconnect, and cannot depend on the existing ones in the present disconnect, right?