I'm installing a 3-phase panel with 2 - 50A 3 pole breakers in it there are no neutral loads.
My Question is where in the code book does it say I don't have to run a neutral.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
If this were service equipment (main panel) 250.24(C) would be applicable.

Roger
 

raider1

Senior Member
Staff member
Location
Logan, Utah
I'm installing a 3-phase panel with 2 - 50A 3 pole breakers in it there are no neutral loads.
My Question is where in the code book does it say I don't have to run a neutral.

A better question would be, where in the code book does it say you have to bring a neutral to a remote panelboard.

Roger pointed out the code section that requires a grounded conductor to be brought to the service disconnecting means. Other than that there is no requirement to bring a grounded conductor to any remote panelboard, this would be a design choice.