Hello--
Today I was working on an old door jamb switch which I thought had gone bad. (As it turned out, the strike plate just needed adjustment, and is working correctly now.) My question pertains to the routine testing I did while I had the switch disconnected.
With the circuit on, I had the expected 110-120 volts between the two wires to the switch.
With the circuit OFF: I had zero resistance between the two wires(!)
With the circuit off and the light bulb removed: back to infinite resistance.
I tested this several times with the bulb in and out; I was consistently reading a connection between the two wires as long as the bulb was in. I don't understand how this could be without shorting the circuit.
Any ideas?
Additional information: since this is old BX wiring, I have the circuit on an arc-fault breaker. There was one place in the house when I first moved in where the ground sheath was the return path for a particular fixture. Once I put the arc-faults in, turning on that light would throw the breaker, which is how I discovered the problem.
Thanks for any advice
--Nathan Rose
Today I was working on an old door jamb switch which I thought had gone bad. (As it turned out, the strike plate just needed adjustment, and is working correctly now.) My question pertains to the routine testing I did while I had the switch disconnected.
With the circuit on, I had the expected 110-120 volts between the two wires to the switch.
With the circuit OFF: I had zero resistance between the two wires(!)
With the circuit off and the light bulb removed: back to infinite resistance.
I tested this several times with the bulb in and out; I was consistently reading a connection between the two wires as long as the bulb was in. I don't understand how this could be without shorting the circuit.
Any ideas?
Additional information: since this is old BX wiring, I have the circuit on an arc-fault breaker. There was one place in the house when I first moved in where the ground sheath was the return path for a particular fixture. Once I put the arc-faults in, turning on that light would throw the breaker, which is how I discovered the problem.
Thanks for any advice