I have an installation that I feel is in violation of a number of NEC sections and would like some other peoples thoughts as well
Here is the set up.
A 45 amp 3 pole breaker supplies the primary side of a 30 KVA 480 delta transformer , the secondary is three phase 240 phase to phase and 120 one phase to midtap. No 120 volt loads are being supplied. From the secondary side, 8 AWGs supply a non fused disconnect right beside the transformer from there 8 AWG is run about a 150? ? 200? to a 60 amp receptacle that in turn supplies a mobile freezer unit.
Here is sort of a one line of it.
480 volt panel > 45 amp breaker > 30 kva transformer > 8 AWG > non fused 60 amp disconnect > 175? 8 AWG > 60 amp receptacle > 60 amp plug > 75? 8/4 rubber cord > refrigeration unit.
Here is what I come up with. Primary side is OK secondary side not so good.
240.21(C) (The installation does not meet any of the options)
210.21(B)(1) (There is no over current protection protecting the receptacle)
It seems to me there could be other violations as well. Any thoughts are appreciated.
Here is the set up.
A 45 amp 3 pole breaker supplies the primary side of a 30 KVA 480 delta transformer , the secondary is three phase 240 phase to phase and 120 one phase to midtap. No 120 volt loads are being supplied. From the secondary side, 8 AWGs supply a non fused disconnect right beside the transformer from there 8 AWG is run about a 150? ? 200? to a 60 amp receptacle that in turn supplies a mobile freezer unit.
Here is sort of a one line of it.
480 volt panel > 45 amp breaker > 30 kva transformer > 8 AWG > non fused 60 amp disconnect > 175? 8 AWG > 60 amp receptacle > 60 amp plug > 75? 8/4 rubber cord > refrigeration unit.
Here is what I come up with. Primary side is OK secondary side not so good.
240.21(C) (The installation does not meet any of the options)
210.21(B)(1) (There is no over current protection protecting the receptacle)
It seems to me there could be other violations as well. Any thoughts are appreciated.