Don, If it went that route wouldn't ground fault indicators be needed?
Could I supply a 60 amp receptacle without OCP?
I still say "no". 210.21(B) says a single receptacle shall have a rating not less than the branch circuit. 210.3 tells us the branch circuit rating is determined by the over current device.
In addition 210.19(C) tells us equipment must be protected by an overcurrent device.
The latitude in 240.21(C(1) for delta-delta or two wire transformers only applies to protection of conductors, not equipment. All of the transformer tap rules require termination at some type overcurrent device(s).