Product Description
GE Type QL midtapped transformer enables the user to transform
three-phase power from 480 Volts primary to 240 Volts second-
ary and have 120 Volt, reduced capacity tap (RCT) single-phase
capability as well. This is because a single-phase midtap is
broughtout of one coil of the unit’s three-phase secondary wind-
ing. These transformers are UL listed, File E-79145.
Application
The Type QL midtapped design can be used wherever there is 480
Volt, three-phase supply available and the load is primarily 240
Volt three-phase with a nominal amount of 120 Volt, single-phase
power required. Normally, in this instance, a small single-phase
as well as a three-phase transformer would be required to
provide the necessary transformation.
Caution:
When utilizing the 120 Volt midtap for single-phase
applications, the single-phase load should not exceed 5 percent
of the three-phase kVA rating. The three-phase kVA load must be
reduced by the same percentage as that added by the single-
phase load. Additional loading beyond 5 percent may cause the
transformer to overheat and fail. If the single-phase load is in
excess of 5 percent, itis recommended that a separate single-
phase unit be used to handle the load.
Type QL Midtapped Transformer