bobster789
Member
- Location
- Edmond, Oklahoma
I have a friend who is asking about a transfer switch for his house for a portable generator.
His house was built in 1966. Service conductors come overhead, into a meter enclosure mounted on an exterior wall.
The 100 amp main panel inside the structure contains a 100 amp circuit breaker used as a main disconnect. However, this "disconnecting means" is NOT "inside nearest the point of entrance of the service conductors".
The main panel is on an interior wall in a utility room. Between this interior wall and the exterior wall where the meter box is the kitchen. Service conductors are routed up the wall from the meter box, across the attic, and down the wall to the panel. Probably 30 conductor feet total.
So the "disconnecting means" is at least 20 feet inside the structure from where the service conductors enter.
Isn't this a violation of 230-70(a)? How did this ever pass inspections in the first place?
His house was built in 1966. Service conductors come overhead, into a meter enclosure mounted on an exterior wall.
The 100 amp main panel inside the structure contains a 100 amp circuit breaker used as a main disconnect. However, this "disconnecting means" is NOT "inside nearest the point of entrance of the service conductors".
The main panel is on an interior wall in a utility room. Between this interior wall and the exterior wall where the meter box is the kitchen. Service conductors are routed up the wall from the meter box, across the attic, and down the wall to the panel. Probably 30 conductor feet total.
So the "disconnecting means" is at least 20 feet inside the structure from where the service conductors enter.
Isn't this a violation of 230-70(a)? How did this ever pass inspections in the first place?