Neutrals, no; grounds, only two, same size, if mfgr. says so.can i put multiple neutrals in 1 hole or just ground wires
Most of them say so......grounds, only two, same size, if mfgr. says so.
I think all the comments are assuming that that the OP is referring to a service panel. But now that you mention it I don't think the OP made that clear.Dont neutrals and egcs have to be isolated from each other?
Dont neutrals and egcs have to be isolated from each other?
Dont neutrals and egcs have to be isolated from each other?
I think all the comments are assuming that that the OP is referring to a service panel. But now that you mention it I don't think the OP made that clear.
200.2(B) states that the continuity of the grounded conductor (neutral) cannot depend on the enclosure carrying the current. Some ground bars don't have a direct connection to the neutral bonding jumper, and only connect at the mounting screws.
In California from my 30+ years of home and business wiring the only place the grounds and neutrals are allowed / required to bond is at a main panel, actually when purchasing a new meter main panel there is only 1 Ground/Neutral Bus which connects directly to the utility return lug. On a sub panel, a flat copper jumper is provided which can be used or not to bond the isolated neutral bar to the distribution enclosure if acting as the originating distribution off the utility reference, I suppose every state has it's own specific guidelines.200.2(B) states that the continuity of the grounded conductor (neutral) cannot depend on the enclosure carrying the current. Some ground bars don't have a direct connection to the neutral bonding jumper, and only connect at the mounting screws.
Best practice is to avoid mixing ground and neutral on the same busbar, even if it is a main service panel. Stick to only the neutral bonding hardware to make this connection, and where necessary to expand the neutral, use separate insulated connectors to generate more terminal positions.
.... But most panels have twice as many holes in the neutral bar than there could be breakers.
...
Some of those older panels did not enough holes especially once we started adding EGs.Not in my experience. More often it's exactly the number of possible breaker poles if you follow the panel labeling strictly. Especially older panels I suppose. It's a real b$#!% if any of the terminal screws get stripped out.
And the original electrician used all of the front holes first.Some of those older panels did not enough holes especially once we started adding EGs.
ome of those older panels did not enough holes especially once we started adding EGs.
I believe they knew we were going to use MWBC back when. Didn't need any extra holes.