Interesting. The local amendments seem to consider that any poured concrete foundation automatically contains a CEE. But, on the other hand, you are not required to connect to it unless it is accessible.Are you in Washington?
Current electrical laws and rules here: http://www.lni.wa.gov/TradesLicensing/Electrical/LawRulePol/LawsRules/default.asp
They said it matters when the building permit was issued to get around it. His was issued on April 16th
Sounds like a workable solution, especially since the AHJ accepted it, although it is not clear from the code language whether a "supplementary" footer that is not actually a structural footer for the building is OK. Chipping down to a piece of rebar and then repairing the concrete has also been discussed as an option. Either one could be less expensive than a ground ring, depending on the soil, etc.I ran into this situation when the framer cut the rebar (and framed over it) that i had installed for a multi-family building. This may or may not be the correct solution, but the AHJ allowed me to dig a supplementary footer next to the service that was 2' deep and 20' long, i installed a 20' piece of rebar (or #4 bare wire) that was raised 2" off of the earth and then had the concrete sub fill it in with concrete. Its an expensive solution, but the framer had to pay for it, so i didn't mind.![]()
I'm supprised that the inspector could be so bold as to not allow 2 ground rods in this case, if it is a new foundation he should have verified there was a UFFER installed before signing off on the inspection prior to pouring it and since he did he should have worked with you.