I have a question. Is the use of Noalox required on aluminum conductors when terminated on al/cu rated lugs in a loadcenter. I would appreciate any input on this subject thanks.
Chris.
Chris.
WHAT??? I'm thinking you might be mixed up about that. If that was true, it would be a million dollars a bottle.Originally posted by wildman:
...there is one for copper to aluminum connections ...
radiopet said:Paul,
Ryan is 100% right in that again if the Manufacturer calls for it in their panel then it must be used...but as a blanket statement it is not the view of the NEC that it has to be used......but clearly allows for it's use.
Hope this clears it up
infinity said:Has anyone seen a panel that required the use of these products?
I will answer your question point-blank: No, I don't use a wire brush.paul32 said:I was going to ask this, and see Ryan did. Why no answers? Is nobody following the directions? On Noalox specificially it says to work the stuff into the conductor using emery cloth or wire brush.