jwelectric said:
David
You have made a couple of statements here that I don?t fully understand and I hope that you will help me to better understand them.
dnem said:
Since deox improves the connection on wire
I was under the impression that the antioxidant impeded the flow of current and its sole purpose was to stop oxidation of the conductor. Being that the antioxidant is not a conductor how can it improve the connection?
It improves the connection by stopping oxidation of the conductor.
I'm going to make some guesses here.
If 2 identical installs were compared with the only difference being one had deox and the other didn't and resistance at different times was measured on a scale of 1 to 10. . I would guess the chart would look something like this:
nondeox, time of install = 2
nondeox, one year later = 7
deox, time of install before applying deox = 2
deox, time of install after applying deox = 3
deox, one year later = 4
jwelectric said:
dnem said:
Wouldn't it be best to just always put it on and not even try to find out if that particular cable requires deox or just recommends it ?
I was also under the impression that it was the termination that required the antioxidant and not the cable. Which cable manufactures are requiring the use of Antioxidants?
Point well taken, the correct way to ask that question would be:
termination requires deox or just recommends it ?
Since all of the junk grade aluminum wire that was used in the past is now gone by code requirement [310.14], I imagine the offending item in a failed test would probably be the lug and more specifically the lack of the necessary surface contact between the lug screw tip or plate and the aluminum conductor. . With aluminim being more pliable than copper, as long as you provide a large contact area and enough squeezing pressure, you should get a decent amount of contact. . I assume the difference in contact area is the reason some test connections fail and others don't.
David