petersonra
Senior Member
- Location
- Northern illinois
- Occupation
- engineer
You have a choice between code compliance and non-compliance.Thank you all for being so generous with your expertise. The existing system is in fact wired with all 6 devices (dock locks) on a single 20amp breaker, and has been since installed in 1996. No one ever recalls a breaker trip. However, I am at this time upgrading these lock controllers, which causes me to review the install to ensure it's code compliant. It seems that, although incredibly unlikely, technically to comply with code, I can't put more than two devices per breaker. I understand sometimes what's practical, and what's legal don't always align. Is there any provision in the code that allows for a deviation based on local engineer review? Seems like I remember seeing something like this before.
I ran into a similar thing once. Had some MV CB's that had motorized operators. The motor only runs for a few seconds at a time, but all five operators were supposed to trip simultaneously under a few cases. Each motor was like 20 Amps at 120 VDC. Five motors = 100 Amps at 120 VDC needed. And only used a few seconds at a time a few times a month.