mark32
Senior Member
- Location
- Currently in NJ
So, an acquaintance had a small gen ATS installed years ago by someone he claims was an electrician. I guess the permit was still open, so the town contacted him and set up a date for an inspector to come and look things over. Among other things, he pointed out that he had two or more grounded conductors under the same individual terminal in the neutral bar within this ATS. He was also red tagged for having a number of romex homeruns entering this enclosure without it's outer jacket in place. The original installer had passed away, so he's bending my ear for some help. At first, I couldn't understand why there were so many neutrals doubled up on the neutral bar. And then I was taken back a bit when I saw that the entire panel was all twins. I asked him to send me the specs on the panel. It turns out, it's only a 12/12 panel, which then made sense as to why there wasn't a large enough neutral bar from the factory to accommodate all of the circuits he jammed into this little panel. Years ago, I came to the conclusion that one is not allowed to install a non-ctl twin in a panel installed after 1968, which is a date I had taken from the packaging on a Square D non-ctl twin breaker. So, did this inspector overlook this, or is it okay to stick a non-ctl twin in a current ctl assembly?