What is up with this exception to 750.31? The service...what?
Exception: Where the overcurrent protection for the power
production source is located more than 3m ( 10') from
point of connection for the electric power production
source to the service, cable limiters or current-limited circuit
breakers for each ungrounded conductor shall be installed
at the point where the electric power production
conductors are connected to the service.
That sounds a bit odd to me, the OCPD should be within 10' of..itself?
:huh:
Isn't it saying:
"If the OCPD for inverter(s) is more than 10' from the service...(???), the inverter OCPD point is the service connection point"...??
Around here, the non-fused is what the POCO wants (outside) and the fused switch is elsewhere for protection, and the fused can be seemingly not within 10 feet, going by the pdf below.
I'm sure someone will disagree with me- I don't agree with myself here...
Seems to me code does not really require OCPD within 10' of a meter or j-box, and the POCO wants one next to the meter. (outside)
(Side note: an overhead "service entrance" where I am includes:OVERHEAD SERVICE CONDUCTORS, DRIP LOOP, O.H. SERVICE-ENTRANCE CONDUCTORS, SERVICE EQUIPMENT)
The reasoning in part I suppose would be so they don't have to get inside homes or businesses to flip the switch, perhaps both emergencies and maintenance?
750.31/exception says "service"- not entrance or conductors or where the point of interconnection is exactly.
So how can there be an exception to place something over 10 feet away which says that you have to put the same something within 10 feet? :huh:
That said, sometimes it is a good idea!
(I think this actually relates to eds' post about the 2 services somehow:
http://forums.mikeholt.com/showthread.php?t=182816 )
I mean... the bold part above of 705.31..."connected to the service." Period. The service...what?
It doesn't say service entrance....but...the service entrance conductors run from the meter to main (house) disconnect.
So when you add PV conductors to those supply side, and you are adding more supply side conductors, until you hit the first fused PV switch/breaker.
Here's a diagram with non-fused switch outside and fused inside:
(So I'm saying the fused switch doesn't have to be 10' from j-box, the j-box is *not* the point where the "power production" is connected to the service. The second, fused PV disco is that point)
https://www9.nationalgridus.com/non_html/DG_sample_1line_B.pdf